I am having trouble reading digital tags from Compactlogix.  It only occurs with some digital tags.  Is there an updated version of the ABCLX driver?  Is there a way to import tags directly into citect to ensure tag names and structures are correct?  I already have failonbaddata = 0 and block =1 in the citect.ini.  When I add one of the problem tags, all ABCLX tags go into error.  I'm not very impressed by the lack of information available for this driver.

Parents
  • Hello Tim
    I use that driver for some time without any problem. Usually for that error can be a typo in the tag name or the tag is not readable from PLC (must be "Read/Write" if want to write on it from the scada, "Read Only" and not "None")
    I think that the information in the help file is enough (file ABCLX.chm in Citect Bin folder)
    Good luck