*** Recall of Citect SCADA 2018 / 2018 R2 Updates (July - October 2020)
Hi everyone,
It's with regret that I share that we have identified a regression in recent Citect SCADA Monthly Updates that can affect the operational view of Alarm information including Alarm Summary, Alarm Counts, and other Alarm-related views, and it’s important that we notify our customers who could potentially be affected.
We have shared this message with potentially affected customers who have downloaded any of the following Monthly Updates;
  • Citect SCADA 2018 Update 22 (Jul 2020)
  • Citect SCADA 2018 Update 23 (Aug 2020)
  • Citect SCADA 2018 Update 24 (Sept 2020)
  • Citect SCADA 2018 Update 25 (Oct 2020)
  • Citect SCADA 2018 R2 Update 08 (Jul 2020)
  • Citect SCADA 2018 R2 Update 09 (Aug 2020)
  • Citect SCADA 2018 R2 Update 10 (Sept 2020)
  • Citect SCADA 2018 R2 Update 11 (Oct 2020)
The set of steps that produces this issue is complex, and involves systems including Alarm Redundancy, a large number of Clients, and events which are causing the Alarm Servers to switch roles and Display Clients to switch their connection. This can occur with cases of Domain Users and/or local Citect users. Most concerning, the occurrence of this can appear to be random, with the outcome being that the Alarm Counts, Alarm Summary and/or Alarm view components may fail silently.
With our strongest recommendation we advise the following actions;
  1. If you haven’t yet implemented any of these Updates, postpone the installation.
  2. If you have implemented any of these Updates, uninstall these Updates and roll-back your implementation to the June 2020 Update, available from the AVEVA Knowledge & Support Center website at https://softwaresupport.aveva.com/. The Uninstallation process needs to be performed individually for each Update listed above.
  3. These Updates should be considered “recalled”; please delete any local copies so they’re not accidentally installed in future.
  4. If you have shared any of the above Updates with someone else, please also share this message with them.
For a Redundant configuration, our recommended order would be to first roll-back Primary Servers (across all Clusters, if required), followed by Clients, and finally any Standby Servers.
If you have any questions or concerns regarding the roll-back procedure for your Citect SCADA system, please reach out to your local Distributor and/or AVEVA Support team for specific advice – they will be your best contact for any questions.
Our investigations into the root cause of this issue are ongoing, and we will be publishing a new Update to resolve this issue as soon as possible. Unfortunately, I’m not yet able to forecast when a new Update might be available.
We have also taken the decision to delay the release of the November Update for both Citect SCADA 2018 & 2018 R2 versions as we prioritise the investigation and resolution of this issue, which is our highest development priority. I’ll provide further updates when I have more news regarding this investigation and the availability of a new Update.
I sincerely apologise for the inconvenience.
Kind Regards,
Brad Shaw
Product Manager – SCADA/HMI
  • Hi Michael,
    I was sure I replied, maybe this will appear twice.
    You only need to apply the new [Alarm]JulOct20OnlineUpgrade=1 parameter on your two Alarm Servers. We recommend it is removed once all other Servers and Clients are upgraded to this same November 2020 Update.
    Brad.
  • Hi everyone,
    Is anyone else experiencing problems with the alarms servers using the December 2020 update?
    Our system consists of 2 redundant I/O, alarm, trend, report servers & 2 display clients as terminal servers.
    We had the update 23 (Aug 2020) installed in our servers when the recall was announced. The only issue we had noticed at that time was the alarm process not responding during the process restart, so we proceeded with the roll-back to the update June 2020 following the instructions of the recall.
    In January, we created 40 new users in the system due to a request from the operations team. Since then, we started to have "random" problems displaying the alarms. Basically, the alarm page stops being updated in the display using cicode functions AlarmDsp() and AlarmDspLast(). The alarm log device is working fine as well as playing a .wav file when an alarm is active.
    One of the attempts to solve the problem was the installation of the December 2020 update following the regular sequence: 1) primary server; 2) standby server and 3) display clients, but the issue persists.
    We noticed that when an issue occurs, it is possible to return to regular operation when one of the current users logs off. We also tested restarting the alarm process. Sometimes the restart of the process in the standby server is enough, but in other cases we need to restart just the primary. Currently, we are restarting the alarm process of the standby server every hour, which reduced the occurrence of the issue, but did not solve it.
    I am in contact with Citect support, but I'd like to hear the opinion of the participants of this forum.
    Please, let me know if you have any suggestions.
    Thanks,
    Igor
  • Hi ,
    I'm sorry to hear this problem still persists for you after installing the December update.
    I would recommend you try take note of which Alarm Server the client is connected to when the problem occurs (check the Client kernel, "page table tran" window for details). It sounds from your description that the problem could be impacting Standby Server.
    Just to clarify default client behaviour, the client will stay connected to the server once connected, unless there is a shutdown or interruption on the server side. It won't switch to another server under normal circumstances. This behaviour occurs for Trend, Alarm and Report Servers. While the IO behaves differently by default. It will always switch to the "best available" IODevice, which could mean it switches from Standby to Primary under normal operations. There is a parameter to override the default behaviour for Alarm clients, such that they will prefer one specific server over the other. See "[ClusterName.ServerType]Priority=" to achieve this.
    Please continue to work with AVEVA support to help diagnose this issue. I haven't heard of any other cases with this same issue.
    Please double check what patch/update is applied on all your machines (Server and client), make sure any special parameters have been removed (only required for customers who upgraded from July-Oct patch to Nov).
    Kind regards
    Olivier
  • Yes we are having very similar issues. We have been experiencing issues with the alarm servers since we upgraded to Citect 2018 last summer. We have several users who will regularly change areas on various clients. The clients will stop showing alarms for other areas even though they have the areas in question.
    We believe it is somehow related to the users as logging in/out with different user accounts seems to produce different results. There were 2 bugs fixed in update 8, 66515 and 66467, these indicate that there were known issues with the alarm servers/clients and user accounts.
    We have been in regular contact with support but so far we have no solution to the issues.
    Steve
  • Hello team,
    Thank you for your contributions. I forgot to mention that there is a view only client in our architecture, which had June 2020 update installed. We fixed it today and all machines are currently with the December 2020 update installed.
    We had no occurrence of the issue in the past 18 hours. The alarm process of the standby server keeps restarting every hour and the "[ClusterName.ServerType]Priority=" remains as default.
    Steve, just to confirm, is your system currently running with December 2020 update? The occurrence of the issue has intensified after we created the new users and indeed logging in/out became more frequent.
    Regards,
    Igor
  • Yes we are running the December 2020 update. We have many clients and they do get logged in and out regularly. We only have a few user accounts, but the issues we are experiencing do seem to revolve around users and areas.
    Thanks,