Citect SCADA 7.20 – Trend Only Showing Real-Time, No Historical Data.

Hi everyone,

I'm using Citect SCADA version 7.20 and facing an issue where the trend system only shows real-time data.

Historical data is not appearing when I scroll back or try to view past time ranges.
I've already followed all configuration steps as outlined in the official manual, including:

- Trend tags are configured with logging enabled
- Log Device is set to `Trend`
- Runtime is running without errors
- Disk space is sufficient
- No error messages appear in runtime or event logs

Is there anything else I might be missing?
Do I need to manually configure file paths or trend file settings in this version?

Also, would upgrading to version 7.30 potentially resolve this issue?
I’d really appreciate any recommendations or tips from anyone who has experience with this.

Thanks in advance!
**Sasin**

  • No problem. I hope it will fix things for you.

    Please also note Erik's post about reviewing your trend tag's Period, Time, and No. Files parameters (and possibly also the Sample Period).
    After any changes to these trend tag properties it is necessary to delete your trend files from the data folder. On a restart of the trend server new files will be created, with the correct layout.