Citect Scada 2018 -Evaluation- Real/Integer Value Unpack to Boolean

Hi,

I've just started evaluating Citect Scada 2018, using the SA_example project, is there a way to unpack a real values (16bit) to boolean values?

I want to read an real/integer value from the Controller, then unpack it to 16 boolean tag within the Citect for use as statuses. 

Thanks for any input,

Regards,

Rune

Parents
  • Hi Rune,

    2 more options :
    1) just use the experession directly on the status you want to display
    2) use Calculated variables and set the address to the expression (BITAND) , see
    https://gcsresource.schneider-electric.com/Citect/WebHelp/citect2018/Content/Calculated_Variables.htm
Reply
  • Hi Rune,

    2 more options :
    1) just use the experession directly on the status you want to display
    2) use Calculated variables and set the address to the expression (BITAND) , see
    https://gcsresource.schneider-electric.com/Citect/WebHelp/citect2018/Content/Calculated_Variables.htm