How to change 2 register data under modbus protocol in citect v7.10
Hi
I am currently trying to read the edmi MK6N data with a floating data type in citect v7.0 SP4 before. I have tried reading the metring data via modpoll and citect, but the reading of kwh shows that it does not match the actual device.
after I looked at the modpoll where kwh data is on base 1 but in the citect read on base 0, I have tried changing the citect.ini parameter (Floatmode = 1 or 2) but the kwh value is still not appropriate.
can you tell me how to change the 2 registers and get the base 1 value through the cicode script?
Thank's
Irwin.s
  • Hi Irwin,
    Are you sure the register index is correct? E.g. is the starting address odd or even? 400001 or 400002. The above parameter should work with regards to swapping the words within the float around. You can confirm this by enabling debugging. If you still experience issues I'd recommend getting in contact with Citect Support.
    Kind regards
    Olivier
  • Hi Oliver
    Ya sure  the register is correct, The following I provide information about the register address and the citect.ini configuration parameter :
    No. Description              Address Unit
    1 Voltage L1 - N               40001  V
    2 Voltage L2 - N               40003  V
    3 Voltage L3 - N               40005  V
    4 Current A                       40007  A
    5 Current B                       40009  A
    6 Current C                       40011  A
    7 Active Power Total         40013 Watt
    8 Reactive Power Total     40015 Var
    9 Apparent Power Total    40017 Va
    10 Frequency                    40019 Hz
    11 Power Factor                40021
    12 Total Import Wh            40023 Wh
    13 Total Export Wh            40025 Wh
    14 Total Import Varh          40027 Varh
    15 Total Export Varh          40029 Varh
    16 Total Import Vah           40031 Vah
    17 Total Export Vah           40033 Vah
    Citect.ini parameter
    FloatMode = 1
    IniType = 3
    IniUnitAddress = 2
    RegisterBitReserve = 1
    SendBCDSwap = 1
    and I sent photo when reading the modpoll and citect, please download link dropbox below :
    https://www.dropbox.com/s/ouwbve2ts80izht/Modpoll%20and%20citect%20reading%20to%20edmi%20device.rar?dl=0