some variables tags were not found.Tell me please how to solve the problem?

Hello!
I ask for help in solving the following problem. I’ll only say in advance how I study citect. More precisely, on the existing facility I study and try to make changes to the project.
In the PLC, modicon 580 created a variable with underwriting in the% MW register and trying to bring it into scada.
In scada created Tag, previously created equipment, type.Tag compiled, Linked Yes.
When displaying the variable in the graphical editor, I select the variable and the inscription appears some variables tags were not found.

Further I carry out RUN of the project. My variable is red with a value of 0, which is different from reality.

Tell me please how to solve the problem?

Parents
  • Hello Yuri,

    Maximum variable tag which is appear in citect graphic builder is limited to 500 as i remember.
    Refer to "Citect Project Editor" page, from Tools>Option find "Maximum list box item" and change the quantity as you may need. Also it can be change from INI parameter MaxHelpRec.

    BR,
    Amin
Reply
  • Hello Yuri,

    Maximum variable tag which is appear in citect graphic builder is limited to 500 as i remember.
    Refer to "Citect Project Editor" page, from Tools>Option find "Maximum list box item" and change the quantity as you may need. Also it can be change from INI parameter MaxHelpRec.

    BR,
    Amin