Citect Scada 2018 SA - Time Stamped Alarms Not showing correct time in Page

Hi,

Alarms setup as "Time Stamped Alarm" using Miilisecond Counter from the Controller. 

In the controller I have

Hr = 11

Min = 8

Sec = 39

Millisec = 619

Adding these together the time value sent as Integer to Citect Scada 2018 SA is 40119619 -this value I can display in Citect screen through a numeric value. 

The time stamp in the alarm page is 03:04:33

My Paramter config is set like:

FORMAT ->ALARM: {PriorityAndState,25}{OnDate,80}{OnTime,90}{Name,250}{State,40}{Equipment,220}{Item,160}{Category,60}

I see from help file that {OnMilli,n} might be used but dont know how to add it as the time format comes up like hh:mm:ss.mmm

When I add {OnMilli,n}  it comes as a new column in the alarm page. 

BIG Question! How to get correct time stamp in the alarm page? 

Thanks for any input,

Rune

Parents
  • Actually this issue happens each time you restart the RunTime independent if there are any alarms active in the alarm page.
    Clearly the system must handle a RunTime ReStart without the need for a new compile?
Reply
  • Actually this issue happens each time you restart the RunTime independent if there are any alarms active in the alarm page.
    Clearly the system must handle a RunTime ReStart without the need for a new compile?