Citect Scada 2018 SA - Time Stamped Alarms Not showing correct time in Page

Hi,

Alarms setup as "Time Stamped Alarm" using Miilisecond Counter from the Controller. 

In the controller I have

Hr = 11

Min = 8

Sec = 39

Millisec = 619

Adding these together the time value sent as Integer to Citect Scada 2018 SA is 40119619 -this value I can display in Citect screen through a numeric value. 

The time stamp in the alarm page is 03:04:33

My Paramter config is set like:

FORMAT ->ALARM: {PriorityAndState,25}{OnDate,80}{OnTime,90}{Name,250}{State,40}{Equipment,220}{Item,160}{Category,60}

I see from help file that {OnMilli,n} might be used but dont know how to add it as the time format comes up like hh:mm:ss.mmm

When I add {OnMilli,n}  it comes as a new column in the alarm page. 

BIG Question! How to get correct time stamp in the alarm page? 

Thanks for any input,

Rune

Parents
  • Have you tried deleting the Alarm Database (while Citect RunTime is not running)?
    If you reconfigure alarms that have already triggered previously, then your changes will not reflect on those alarms.
    Deleting the database will correct this, but you will lose your alarm history.

    This default behaviour can be changed by setting [Alarm]UseConfigLimits=1, but please consult the Help on this parameter as it can have side effects.
Reply
  • Have you tried deleting the Alarm Database (while Citect RunTime is not running)?
    If you reconfigure alarms that have already triggered previously, then your changes will not reflect on those alarms.
    Deleting the database will correct this, but you will lose your alarm history.

    This default behaviour can be changed by setting [Alarm]UseConfigLimits=1, but please consult the Help on this parameter as it can have side effects.