Reading data from PM810 over EGX150

Hi,

I am trying to read data from a PM810 meter connected through an EGX-150 gateway. I have tried with a generic Modbus driver, than tested with a generic Modbus scanner. The result is always the error code 04.

Have you encountered such a situation?

Thanks,

Arian

Parents
  • Hi Arian,
    I think you should be using the MODNET driver in Citect, since the EGX-150 is connected to Citect via Ethernet. It will then strip out the appropriate payload and transfer as a pure Modbus command onto the RS485 link.
    Make sure you have defined the PM810 Modbus Address in the Address field of the IODevice form.
    If you can't get the generic Modbus scanner working, it might be worth contacting Schneider Electric support to help troubleshoot it further.
    Kind regards
    Olivier