Citectscada 2018

Encountered the following problem:
1. configured the OFS server through the OFS configurator, through the OFS client checked the connection. Connection successful, variables visible.
2. Configure Scadacitect 2018.
3. created a test page, output a variable, run the project, the variable is 0 (which does not match), in the OPC server the number of client connections is 0. There is an error in Citect IOserver not found, Cluster not found.
4. used as the OFSOPC driver in the m580 folder.
5. It is worth noting that OFS 3.61 as part of Citectscada 2018 is installed on the server Windows 2012R2.

Please help if possible.
Parents
  • Normally, no Citect.ini settings are needed for OFSOPC to work.
    Most important thing is that the address field of your I/O device has to match the PLC name in the OFS configuration tool.
    Have you run the Citect Computer Setup Wizard, and does it recognize your setup as a Server configuration? Or does it say Client only configuration?
Reply
  • Normally, no Citect.ini settings are needed for OFSOPC to work.
    Most important thing is that the address field of your I/O device has to match the PLC name in the OFS configuration tool.
    Have you run the Citect Computer Setup Wizard, and does it recognize your setup as a Server configuration? Or does it say Client only configuration?