WSAENOTSOCK 10038 error on polling with Modnet driver

Hi,

we have a problem with connecting Citect with generic modbus device (standalone discrete I / O Module)

through Modnet driver. After Runtime restart we have a error WSAENOTSOCK 10038 error (syslog.IOServer.Cluster_1.IOServer_2 log file).

 After a few minutes connection is restored and system is working fine until next restart.

Connection parameters in .ini file:  MaxPending=2, Block=250, Retry=0, Delay=0, Timeout=1000, PollTime=0, WatchTime=30000.

Modbus Pool with this device works without problem. 

We are using  Version 7.50 Service Pack Patch 13[5].

Log in included file 

citect_logs.txt

Thanks.

Parents
  • Hi Olivier,

    OS is Windows 7 Professional Service Pack 1, MODNET v2.09.07.00001. I don't know how to determine a TCPIP board driver version. It's some sort of OS level driver?

    Citect.ini file

    [AddressForwarding]
    LicenseStore = 27010@127.0.0.1
    
    [Alarm]
    IsolationDetectIP1 = 
    IsolationDetectIP2 = 
    SavePeriod = 600
    SavePrimary = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\SuperManchar_Manchar2
    SaveSecondary = 
    ScanTime = 500
    #Set to '[RUN]:wav\alarm.wav' by Disp on 25.07.2018 15:17:10.
    Sound1 = [RUN]:wav\alarm.wav
    #Set to '2000' by Disp on 25.07.2018 15:18:20.
    Sound1Interval = 2000
    #Set to '[RUN]:wav\alarm1.wav' by Disp on 25.07.2018 15:17:25.
    Sound2 = [RUN]:wav\alarm1.wav
    #Set to '2000' by Disp on 25.07.2018 15:18:29.
    Sound2Interval = 2000
    #Set to '[RUN]:wav\BEEPER.wav' by Disp on 25.07.2018 15:17:44.
    Sound3 = [RUN]:wav\BEEPER.wav
    #Set to '2000' by Disp on 25.07.2018 15:18:38.
    Sound3Interval = 2000
    SummaryLength = 1000
    SummaryTimeout = 60
    
    [Alarm.Cluster1.AlarmServer1]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = AlarmServerStartup()
    
    [Alarm.Cluster_1.Alarm_1_P]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [Animator]
    FastDisplay = 1
    FullScreen = 2
    
    [Backup]
    BackupPath = F:\SuperManchar_2019_07_29.ctz
    Compress = 1
    DeleteAll = 1
    Encrypt = 0
    Operation = 0
    Recurse = 1
    RestoreInclude = 0
    SaveCompiled = 1
    SaveInclude = 0
    SaveiniFiles = 1
    
    [Client]
    Clusters = Cluster_1
    ComputerRole = 0
    CPU = 0,1,2,3
    Events = Save2hGas,Save2hOil,SaveDayGas,SaveDayOil
    #Set to '1000000' by Disp on 05.04.2018 18:14:38.
    EvictTimeout = 2000000
    FullLicense = 0
    PartOfTrustedNetwork = 1
    StartupCode = StartUp
    TagReadCachedMode = 3
    WaitForConnectAtStartup = 0
    
    [CtCicode]
    BreakAllThreads = 0
    BreakOnError = 0
    Child Window State = 3
    ForeBreakWarning = 1
    Main Window = 2,3,-1,-1,-1,-1,694,332,1654,945
    SaveBreakpoints = 1
    
    [CTDRAW.genie.default]
    file.both = tab_alarms
    file.normal = 
    file.reference = 
    file.super = 
    page.both = row_02
    page.normal = 
    page.reference = 
    page.super = 
    
    [CTDRAW.library.default]
    file = buttons
    linked = 1
    page = xppressed
    project = 
    
    [CTDRAW.pages]
    page0 = SuperManchar,Main
    page1 = SuperManchar,Diag
    page2 = JenniesAndSymbols,FireSettings
    page3 = SuperManchar_Manchar13,Diag
    
    [CtDraw.RSC]
    BackColor = 0x006095ca
    GridCX = 8
    GridCY = 8
    GridX = 0
    GridY = 0
    GuideHorz = 
    GuideVert = 
    ImportFile = C:\Users\Disp\Desktop\����������\3.png
    ListSystemPages = 1
    OldTools = 1
    SwapFromColorA = 0x00ffffff
    SwapFromColorB = 0x00ffffff
    SwapToColorA = 0xffffffff
    SwapToColorB = 0xffffffff
    
    [CTDRAW.status]
    status = 1
    sTools = 1
    
    [CTDRAW.template.default]
    linked = 1
    page = Normal@-XGA
    resolution = 3
    style = Tab_Style_1
    titlebar = 0
    
    [CTDRAW.toolboxes]
    otools = 1719,151,1
    toolbar = 0,0,0
    tools = 1812,301,1
    
    [CTDRAW.Versions]
    ctDraw = 1
    
    [CTDRAW.windowplacement]
    main = 0,9,-32000,-32000,-1,-1,-8,-8,1924,1048
    zoom = 175,156,384,216,0
    
    [CtEdit]
    ANSIToOEM = 0
    Backup = 
    Bin = C:\Program Files (x86)\Schneider Electric\Vijeo Citect 7.50\Bin
    CICODEEDITOR = ctcicode.exe
    COMPILEENQUIRY = 0
    CompileErrorForm = 1
    Config = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\Config
    CONFIRMPACKING = 0
    Copy = 
    Data = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\Data
    DbFiles = 80
    DefaultProtocolID = 1396
    DISABLEUSERFUNCTIONS = 0
    EXTENDED = 1
    IncrementalCompile = 1
    INFORMRECORDCHANGE = 1
    LASTDATABASE = SuperManchar
    LASTDATABASEPATH = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\SuperManchar
    Logs = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\Logs
    MaxHelpRec = 5000
    PAGESIZE = 59
    PrintFont = Courier New
    PrintPoint = 6
    REPORTEDITOR = write.exe
    Run = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\SuperManchar
    SEARCHDELAY = 3
    SHOWDEL = 0
    SHOWPAGEMENU = 0
    Starter = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\Starter
    Upgrade = 0
    User = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User
    WINDOW = 0,9,-32000,-32000,-1,-1,574,142,1536,963
    
    [CtExplore]
    DefaultTemplateBackgoundColorRGB = 229,229,229
    DefaultTemplateResolution = HD768
    DefaultTemplateStyle = SxW_Style_1
    DefaultTemplateTitleBar = 1
    DISPLAYICON = 26093
    InitSelection = Pages
    SHOWSYSTEMPROJECTS = 1
    SPLITTER = 372,0
    WINDOW = 9,960,0,1920,1040
    
    [CtSetup]
    CustomSetup = 1
    
    [Debug]
    ForeGroundOnError = 1
    Menu = 1
    RemoteDebug = 0
    Shutdown = 1
    StartDebuggerOnError = 0
    
    [DIALOG]
    COMPILE =743,458,1177,753
    
    [DRAW]
    Mode = 7
    
    [Event]
    Server = 1
    
    [Format]
    #Set to '{Date,80}{Time,80}{Tag,120}{Name,120}{Desc, 120}' by Disp on 03.05.2018 10:41:20.
    Alarm = {Date,80}{Time,80}{Tag,120}{Name,120}{Desc, 120}
    #Set to '{Date,80}{Time,80}{Tag,120}{Name,120}{Desc, 120}' by Disp on 03.05.2018 11:38:24.
    Summary = {Date,80}{Time,80}{Tag,120}{Name,120}{Desc, 120}
    
    [General]
    Multiprocess = 1
    
    [Internet]
    Server = 0
    
    [IOServer.Cluster1.IOServer]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = Startup
    
    [IOServer.Cluster1.IOServer1]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = 
    
    [IOServer.Cluster_1.IOServer_1]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [IOServer.Cluster_1.IOServer_2]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [Kernel]
    WINDOWPOSITION =1,114,103,1554,863
    Windows =0
    
    [Kernel.WindowPositions]
    Beeline_Realise = 0,0,0,146,28
    Driver = 0,9,7,77,19
    Example = 0,0,0,146,28
    General = 0,0,0,73,22
    JenniesAndSymbols = 0,0,0,146,28
    Library_Controls = 0,0,0,146,28
    Main =6,0,0,146,28
    Memory = 0,0,0,80,20
    NetBIOS Window - ESC to terminate = 0,0,0,75,15
    perenos = 0,0,0,146,28
    SuperManchar =0,0,0,146,28
    SuperManchar_Manchar = 0,0,0,146,28
    SuperManchar_Manchar1 = 0,0,0,146,28
    SuperManchar_Manchar10 = 0,0,0,146,28
    SuperManchar_Manchar11 = 0,0,0,146,28
    SuperManchar_Manchar12 = 0,0,0,146,28
    SuperManchar_Manchar2 = 0,0,0,146,28
    SuperManchar_Manchar3 = 0,0,0,146,28
    SuperManchar_Manchar4 = 0,0,0,146,28
    SuperManchar_Manchar5 = 0,0,0,146,28
    SuperManchar_Manchar6 = 0,0,0,146,28
    SuperManchar_Manchar7 = 0,0,0,146,28
    SuperManchar_Manchar8 = 0,0,0,146,28
    SuperManchar_Manchar9 = 0,0,0,146,28
    SxW_Style_Include = 0,0,0,146,28
    Table = 0,0,0,80,20
    test_modbus_link = 0,0,0,146,28
    testUserCreate = 0,0,0,146,28
    text = 0,0,0,146,28
    Unit = 0,0,0,75,14
    
    [LAN]
    Node = unknown
    TCPIP = 0
    
    [Language]
    #Set to 'Russian(Russia)' by Disp on 06.09.2018 12:18:50.
    LocalLanguage = Russian(Russia)
    
    ! #CSE:UserItem#
    [Modnet]
    #Set to '1' by Disp on 01.08.2019 14:20:06.
    Debug = 1
    #Set to '* ALL' by Disp on 01.08.2019 14:19:49.
    DebugStr = * ALL
    #Set to '10' by Disp on 01.08.2019 15:57:14.
    Delay = 10
    #Set to '400471' by Disp on 31.07.2019 16:43:12.
    InitVar = 400471
    #Set to '3' by Disp on 31.07.2019 16:43:42.
    InitVarType = 3
    #Set to '0' by Disp on 31.07.2019 16:50:04.
    Polltime = 0
    #Set to '3' by Disp on 01.08.2019 15:37:27.
    Retry = 3
    
    [OID]
    #Set to '1' by Disp on 09.04.2018 10:33:22.
    Reset = 0
    
    [Page]
    Startup = Main
    
    [ProcessAnalyst]
    LanguagePath.Chinese = zh-cn
    LanguagePath.Chinese(Simplified, PRC) = zh-cn
    LanguagePath.English = en
    LanguagePath.French = fr
    LanguagePath.French(France) = fr
    LanguagePath.German = de
    LanguagePath.German(Germany) = de
    LanguagePath.Italian = it
    LanguagePath.Italian(Italy) = it
    LanguagePath.Japanese = ja
    LanguagePath.Japanese(Japan) = ja
    LanguagePath.Korean = ko
    LanguagePath.Korean(Korea) = ko
    LanguagePath.Portuguese = pt
    LanguagePath.Portuguese(Brazil) = pt-br
    LanguagePath.Russian = ru
    LanguagePath.Russian(Russia) = ru
    LanguagePath.Spanish = es
    LanguagePath.Spanish(Spain) = es
    LanguagePath.Swedish = sv
    
    [Recent File List]
    File1 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\JenniesAndSymbols\Fire_Task.ci
    File2 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\JenniesAndSymbols\service.ci
    File3 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\JenniesAndSymbols\SQLDevice.ci
    File4 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\JenniesAndSymbols\TimeFilter.ci
    File5 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\Library_Controls\_Internal_AlarmFilterTransfer.ci
    File6 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\Library_Controls\_Internal_AlarmFilterTable.ci
    
    [Report]
    InhibitEvent = 1
    RunStandby = 0
    Startup = 
    
    [Report.Cluster1.ReportServer1]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = 
    
    [Report.Cluster_1.Report_1_P]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [Server]
    AutoLoginMode = 1
    EWSAllowAnonymousAccess = 0
    
    [SPC]
    AlarmBufferSize = 39
    
    [Trend]
    InhibitEvent = 1
    
    [Trend.Cluster1.TrendServer1]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = 
    
    [Trend.Cluster_1.Trend_1_P]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [Win]
    AltSpace = 1
    Configure = 1
    
    

    Thanks

Reply
  • Hi Olivier,

    OS is Windows 7 Professional Service Pack 1, MODNET v2.09.07.00001. I don't know how to determine a TCPIP board driver version. It's some sort of OS level driver?

    Citect.ini file

    [AddressForwarding]
    LicenseStore = 27010@127.0.0.1
    
    [Alarm]
    IsolationDetectIP1 = 
    IsolationDetectIP2 = 
    SavePeriod = 600
    SavePrimary = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\SuperManchar_Manchar2
    SaveSecondary = 
    ScanTime = 500
    #Set to '[RUN]:wav\alarm.wav' by Disp on 25.07.2018 15:17:10.
    Sound1 = [RUN]:wav\alarm.wav
    #Set to '2000' by Disp on 25.07.2018 15:18:20.
    Sound1Interval = 2000
    #Set to '[RUN]:wav\alarm1.wav' by Disp on 25.07.2018 15:17:25.
    Sound2 = [RUN]:wav\alarm1.wav
    #Set to '2000' by Disp on 25.07.2018 15:18:29.
    Sound2Interval = 2000
    #Set to '[RUN]:wav\BEEPER.wav' by Disp on 25.07.2018 15:17:44.
    Sound3 = [RUN]:wav\BEEPER.wav
    #Set to '2000' by Disp on 25.07.2018 15:18:38.
    Sound3Interval = 2000
    SummaryLength = 1000
    SummaryTimeout = 60
    
    [Alarm.Cluster1.AlarmServer1]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = AlarmServerStartup()
    
    [Alarm.Cluster_1.Alarm_1_P]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [Animator]
    FastDisplay = 1
    FullScreen = 2
    
    [Backup]
    BackupPath = F:\SuperManchar_2019_07_29.ctz
    Compress = 1
    DeleteAll = 1
    Encrypt = 0
    Operation = 0
    Recurse = 1
    RestoreInclude = 0
    SaveCompiled = 1
    SaveInclude = 0
    SaveiniFiles = 1
    
    [Client]
    Clusters = Cluster_1
    ComputerRole = 0
    CPU = 0,1,2,3
    Events = Save2hGas,Save2hOil,SaveDayGas,SaveDayOil
    #Set to '1000000' by Disp on 05.04.2018 18:14:38.
    EvictTimeout = 2000000
    FullLicense = 0
    PartOfTrustedNetwork = 1
    StartupCode = StartUp
    TagReadCachedMode = 3
    WaitForConnectAtStartup = 0
    
    [CtCicode]
    BreakAllThreads = 0
    BreakOnError = 0
    Child Window State = 3
    ForeBreakWarning = 1
    Main Window = 2,3,-1,-1,-1,-1,694,332,1654,945
    SaveBreakpoints = 1
    
    [CTDRAW.genie.default]
    file.both = tab_alarms
    file.normal = 
    file.reference = 
    file.super = 
    page.both = row_02
    page.normal = 
    page.reference = 
    page.super = 
    
    [CTDRAW.library.default]
    file = buttons
    linked = 1
    page = xppressed
    project = 
    
    [CTDRAW.pages]
    page0 = SuperManchar,Main
    page1 = SuperManchar,Diag
    page2 = JenniesAndSymbols,FireSettings
    page3 = SuperManchar_Manchar13,Diag
    
    [CtDraw.RSC]
    BackColor = 0x006095ca
    GridCX = 8
    GridCY = 8
    GridX = 0
    GridY = 0
    GuideHorz = 
    GuideVert = 
    ImportFile = C:\Users\Disp\Desktop\����������\3.png
    ListSystemPages = 1
    OldTools = 1
    SwapFromColorA = 0x00ffffff
    SwapFromColorB = 0x00ffffff
    SwapToColorA = 0xffffffff
    SwapToColorB = 0xffffffff
    
    [CTDRAW.status]
    status = 1
    sTools = 1
    
    [CTDRAW.template.default]
    linked = 1
    page = Normal@-XGA
    resolution = 3
    style = Tab_Style_1
    titlebar = 0
    
    [CTDRAW.toolboxes]
    otools = 1719,151,1
    toolbar = 0,0,0
    tools = 1812,301,1
    
    [CTDRAW.Versions]
    ctDraw = 1
    
    [CTDRAW.windowplacement]
    main = 0,9,-32000,-32000,-1,-1,-8,-8,1924,1048
    zoom = 175,156,384,216,0
    
    [CtEdit]
    ANSIToOEM = 0
    Backup = 
    Bin = C:\Program Files (x86)\Schneider Electric\Vijeo Citect 7.50\Bin
    CICODEEDITOR = ctcicode.exe
    COMPILEENQUIRY = 0
    CompileErrorForm = 1
    Config = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\Config
    CONFIRMPACKING = 0
    Copy = 
    Data = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\Data
    DbFiles = 80
    DefaultProtocolID = 1396
    DISABLEUSERFUNCTIONS = 0
    EXTENDED = 1
    IncrementalCompile = 1
    INFORMRECORDCHANGE = 1
    LASTDATABASE = SuperManchar
    LASTDATABASEPATH = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\SuperManchar
    Logs = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\Logs
    MaxHelpRec = 5000
    PAGESIZE = 59
    PrintFont = Courier New
    PrintPoint = 6
    REPORTEDITOR = write.exe
    Run = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\SuperManchar
    SEARCHDELAY = 3
    SHOWDEL = 0
    SHOWPAGEMENU = 0
    Starter = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\Starter
    Upgrade = 0
    User = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User
    WINDOW = 0,9,-32000,-32000,-1,-1,574,142,1536,963
    
    [CtExplore]
    DefaultTemplateBackgoundColorRGB = 229,229,229
    DefaultTemplateResolution = HD768
    DefaultTemplateStyle = SxW_Style_1
    DefaultTemplateTitleBar = 1
    DISPLAYICON = 26093
    InitSelection = Pages
    SHOWSYSTEMPROJECTS = 1
    SPLITTER = 372,0
    WINDOW = 9,960,0,1920,1040
    
    [CtSetup]
    CustomSetup = 1
    
    [Debug]
    ForeGroundOnError = 1
    Menu = 1
    RemoteDebug = 0
    Shutdown = 1
    StartDebuggerOnError = 0
    
    [DIALOG]
    COMPILE =743,458,1177,753
    
    [DRAW]
    Mode = 7
    
    [Event]
    Server = 1
    
    [Format]
    #Set to '{Date,80}{Time,80}{Tag,120}{Name,120}{Desc, 120}' by Disp on 03.05.2018 10:41:20.
    Alarm = {Date,80}{Time,80}{Tag,120}{Name,120}{Desc, 120}
    #Set to '{Date,80}{Time,80}{Tag,120}{Name,120}{Desc, 120}' by Disp on 03.05.2018 11:38:24.
    Summary = {Date,80}{Time,80}{Tag,120}{Name,120}{Desc, 120}
    
    [General]
    Multiprocess = 1
    
    [Internet]
    Server = 0
    
    [IOServer.Cluster1.IOServer]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = Startup
    
    [IOServer.Cluster1.IOServer1]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = 
    
    [IOServer.Cluster_1.IOServer_1]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [IOServer.Cluster_1.IOServer_2]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [Kernel]
    WINDOWPOSITION =1,114,103,1554,863
    Windows =0
    
    [Kernel.WindowPositions]
    Beeline_Realise = 0,0,0,146,28
    Driver = 0,9,7,77,19
    Example = 0,0,0,146,28
    General = 0,0,0,73,22
    JenniesAndSymbols = 0,0,0,146,28
    Library_Controls = 0,0,0,146,28
    Main =6,0,0,146,28
    Memory = 0,0,0,80,20
    NetBIOS Window - ESC to terminate = 0,0,0,75,15
    perenos = 0,0,0,146,28
    SuperManchar =0,0,0,146,28
    SuperManchar_Manchar = 0,0,0,146,28
    SuperManchar_Manchar1 = 0,0,0,146,28
    SuperManchar_Manchar10 = 0,0,0,146,28
    SuperManchar_Manchar11 = 0,0,0,146,28
    SuperManchar_Manchar12 = 0,0,0,146,28
    SuperManchar_Manchar2 = 0,0,0,146,28
    SuperManchar_Manchar3 = 0,0,0,146,28
    SuperManchar_Manchar4 = 0,0,0,146,28
    SuperManchar_Manchar5 = 0,0,0,146,28
    SuperManchar_Manchar6 = 0,0,0,146,28
    SuperManchar_Manchar7 = 0,0,0,146,28
    SuperManchar_Manchar8 = 0,0,0,146,28
    SuperManchar_Manchar9 = 0,0,0,146,28
    SxW_Style_Include = 0,0,0,146,28
    Table = 0,0,0,80,20
    test_modbus_link = 0,0,0,146,28
    testUserCreate = 0,0,0,146,28
    text = 0,0,0,146,28
    Unit = 0,0,0,75,14
    
    [LAN]
    Node = unknown
    TCPIP = 0
    
    [Language]
    #Set to 'Russian(Russia)' by Disp on 06.09.2018 12:18:50.
    LocalLanguage = Russian(Russia)
    
    ! #CSE:UserItem#
    [Modnet]
    #Set to '1' by Disp on 01.08.2019 14:20:06.
    Debug = 1
    #Set to '* ALL' by Disp on 01.08.2019 14:19:49.
    DebugStr = * ALL
    #Set to '10' by Disp on 01.08.2019 15:57:14.
    Delay = 10
    #Set to '400471' by Disp on 31.07.2019 16:43:12.
    InitVar = 400471
    #Set to '3' by Disp on 31.07.2019 16:43:42.
    InitVarType = 3
    #Set to '0' by Disp on 31.07.2019 16:50:04.
    Polltime = 0
    #Set to '3' by Disp on 01.08.2019 15:37:27.
    Retry = 3
    
    [OID]
    #Set to '1' by Disp on 09.04.2018 10:33:22.
    Reset = 0
    
    [Page]
    Startup = Main
    
    [ProcessAnalyst]
    LanguagePath.Chinese = zh-cn
    LanguagePath.Chinese(Simplified, PRC) = zh-cn
    LanguagePath.English = en
    LanguagePath.French = fr
    LanguagePath.French(France) = fr
    LanguagePath.German = de
    LanguagePath.German(Germany) = de
    LanguagePath.Italian = it
    LanguagePath.Italian(Italy) = it
    LanguagePath.Japanese = ja
    LanguagePath.Japanese(Japan) = ja
    LanguagePath.Korean = ko
    LanguagePath.Korean(Korea) = ko
    LanguagePath.Portuguese = pt
    LanguagePath.Portuguese(Brazil) = pt-br
    LanguagePath.Russian = ru
    LanguagePath.Russian(Russia) = ru
    LanguagePath.Spanish = es
    LanguagePath.Spanish(Spain) = es
    LanguagePath.Swedish = sv
    
    [Recent File List]
    File1 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\JenniesAndSymbols\Fire_Task.ci
    File2 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\JenniesAndSymbols\service.ci
    File3 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\JenniesAndSymbols\SQLDevice.ci
    File4 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\JenniesAndSymbols\TimeFilter.ci
    File5 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\Library_Controls\_Internal_AlarmFilterTransfer.ci
    File6 = C:\ProgramData\Schneider Electric\Vijeo Citect 7.50\User\Library_Controls\_Internal_AlarmFilterTable.ci
    
    [Report]
    InhibitEvent = 1
    RunStandby = 0
    Startup = 
    
    [Report.Cluster1.ReportServer1]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = 
    
    [Report.Cluster_1.Report_1_P]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [Server]
    AutoLoginMode = 1
    EWSAllowAnonymousAccess = 0
    
    [SPC]
    AlarmBufferSize = 39
    
    [Trend]
    InhibitEvent = 1
    
    [Trend.Cluster1.TrendServer1]
    Clusters = Cluster1
    CPU = 
    Events = 
    StartupCode = 
    
    [Trend.Cluster_1.Trend_1_P]
    Clusters = Cluster_1
    CPU = 
    Events = 
    StartupCode = 
    
    [Win]
    AltSpace = 1
    Configure = 1
    
    

    Thanks

Children
No Data