Trend History Files vs variable tag engineering range change

Hi,

I have a variable tag defined with an engineering range of 0-30 DegC, and that variable tag drives a trend tag which is set up to log over 12 trend history (log) files. If I then need to change the engineering range of the variable tag to 0-60 DegC, am I right in saying that the already created and logged to trend history files are not affected by this change and do NOT need to be deleted/re-created? Would they be capable of handling a value of e.g. 55 which the original engineering range would not allow?

As far as I know, deleting the trend history files would only be necessary if one of the timing (No. Files, Period, Time, Sample Period) or Storage Method fields changed on the trend tag definition.

Please confirm.

Thanks

Ash

Parents
  • Hi Erik,

    Thanks for your quick reply. Happily, all my trend tags are defined with Storage Method=Floating Point (8-byte samples), so it seems I can change the source variable tag engineering range and the trend history files will be unaffected.

    That was the answer I was hoping for!

    Thanks,
    Ash
Reply
  • Hi Erik,

    Thanks for your quick reply. Happily, all my trend tags are defined with Storage Method=Floating Point (8-byte samples), so it seems I can change the source variable tag engineering range and the trend history files will be unaffected.

    That was the answer I was hoping for!

    Thanks,
    Ash