ABCLX Driver

Hello All,

i have configured a system where i am using the ABCLX driver ( ControlLogix system PLCs). All are communicating except 1 and the settings are the same.

Below i send the kernel imagem.

Parents
  • lately, with Windows 10, and Citect 2018 and higher, we always do the following
    - install the latest ABCLX driver
    - Add the following in the Citect.ini file
    [ABCLX]
    LostMsgRetry = 3
    LostMsgTimeout = 4000

    we've seen instances where the PLC will respond to 200 tags, but all comms fail when adding an additional tag unless you do the above, I believe all to do with CPU resources, good Luck

    Greg
Reply
  • lately, with Windows 10, and Citect 2018 and higher, we always do the following
    - install the latest ABCLX driver
    - Add the following in the Citect.ini file
    [ABCLX]
    LostMsgRetry = 3
    LostMsgTimeout = 4000

    we've seen instances where the PLC will respond to 200 tags, but all comms fail when adding an additional tag unless you do the above, I believe all to do with CPU resources, good Luck

    Greg