Hi
Anyone got any ideas for communications with the Schneider TM251 MESE Controller - TCPIP MODNET ( Not interested in the OPC Option)
We are using the MODNET30 Driver but cannot directly access the %MX.b memory - Not in the Address Template
So to Address %MX20301.0 in the PLC we need to set the TAG address in Citect to either %MW10150.8 or 410150.8 for the MODNET30 driver.
We are not confident in modifying the MODNET Driver Address DBF template. ( MODNET_PREM.DBF)
So looking for other options where we can put the matching address in the Citect Address for the PLC memory location. i.e %MX10150.8
Driver works fine for the %MW address range with the Citect %MW addressing and the %M and %QX etc.
Machine Expert (M251) does not allow BOOL declaration for the %MW in the PLC like %MW10150.8
Any suggestions or workarounds - help much appreciated.
James Mackenzie
New Zealand