OPC UA Configuration Fails Error: OPC uA status code: '0x80160000'

Dear All,

I'm using Citect2018 and after upgrading OPCUA driver to v3.01.04.00000 can not connect to OPC UA server (Siemens HMI Panel) and at the end of OPC UA Configurator following error is displayed: 

OPC UA Configuration Fails Error: OPC uA status code: '0x80160000' 

Any help is highly appreciated.

Parents
  • Hi , this help is provided without warranty, just what I have seen reported previously:
    [issue] problem with the OPC UA client: it cannot download the tags from the controller or during the Configurator
    [resolution] install the client certificate on the Server
    If you still experience this issue, try contacting Citect support to try further steps to resolve this issue.
Reply
  • Hi , this help is provided without warranty, just what I have seen reported previously:
    [issue] problem with the OPC UA client: it cannot download the tags from the controller or during the Configurator
    [resolution] install the client certificate on the Server
    If you still experience this issue, try contacting Citect support to try further steps to resolve this issue.