Information of field switches in Citect scada

Hi Guys...

How can I get port information of switches in the field into citect scada from Connexium Network Manager program. It was received with snmp but I don't know how.,

Can you help about this topic.

Thanks...

Parents
  • Hi ,
    The best way that I know of is to use the SNMPII driver. This provides the ability to poll status of ports and also setup "SNMP Traps" to get events pushed to Citect (e.g. Port being blocked).
    The SNMPII driver only supports v1 and v2c SNMP messages.
    There is a guide to using this driver on the Support Website:
    https://softwaresupportsp.aveva.com/#/okmimarticle/docid/tn7772
    The setup can be a bit involved, so make sure you read the guide, setup a small test project, then build up from there.
    You might also need to check out the Schneider Electric FAQ for information about your switch, e.g.:
    https://www.se.com/au/en/faqs/FA242769/
    Hope this helps.
Reply
  • Hi ,
    The best way that I know of is to use the SNMPII driver. This provides the ability to poll status of ports and also setup "SNMP Traps" to get events pushed to Citect (e.g. Port being blocked).
    The SNMPII driver only supports v1 and v2c SNMP messages.
    There is a guide to using this driver on the Support Website:
    https://softwaresupportsp.aveva.com/#/okmimarticle/docid/tn7772
    The setup can be a bit involved, so make sure you read the guide, setup a small test project, then build up from there.
    You might also need to check out the Schneider Electric FAQ for information about your switch, e.g.:
    https://www.se.com/au/en/faqs/FA242769/
    Hope this helps.