OPC UA freezing problem

Hi,

Our plant has a Siemens S7-1500 with an OPC UA server. Citect Scada 8.1 (update 28) communicates with logic with the OPC UA client. If, for some reason, Citect cannot read the variables from the logic, the variables will be displayed in #BAD. After a while, all the variables whose value is constantly changing start to show the current value again. Variables with a static value (such as pump status) remain #BAD and do not recover until the Citect IO server is restarted. OPC UA client version is 4.01.04.000.

Is there any parameter to force the OPC UA client to read all variables?

I can't find in-depth information on Citect's OPC UA client, so any help is needed.

Parents Reply
  • Thanks Timo. So, we can eliminate the encryption that caused the original problem. Enabling the backrgound poll means that once an OPC UA  variable tag is subscribed, it will be changed to the "Reporting" mode and always in that mode until the session ends. Without the background poll, those tags on a page will be changed to the "Disabled" mode when you are navigating away from this page. I suspect that the server may not handle well the frequent changes of monitoring modes, especially for those tags with "static" values.