Aveva Plant Scada 2020 R2 update 6 run time manager error

Hi,

I am running Aveva Plant Scada 2020 R2 update 6, while running the project  I am getting 'Runtime manager error' with notification as "cannot connect to the runtime manager service, ensure the service has been started".  I have tried starting runtime manager service manually but could not resolve the error.

below is the screenshot of error. 

/resized-image/__size/1048x588/__key/communityserver-discussions-components-files/1457/aveva-runtime-error.png

any guidance will be much helpful. 

regards,

Piyush

Parents Reply
  • Not sure if you rebooted the machine after Common Platform Service upgraded. Anyway, please check if AVEVA Data Store service is running. If not, manually start it up.

      

    Your problem could be caused by ADS that failed to automatically start up. Without ADS running, Runtime Manager will fail to obtain any security info of the configured project and thus fail to launch the project.