DNPR and plant SCADA 2020R2 Communication Error

Hi All,

I am facing issue  while working with DNPR when i am starting the RT then i am getting single value on the SCADA run time after that no response after the 1 min in kernal i am getting some error message  even during this 1 min there is no change in the values.

     Error_in CMD_17   16 Generic 000011 Driver  00000094 (0x0000005e)

1st START UP OF RUN TIME

After 1 min

 INI PARAMETERS

I need your kind support.

Parents
  • Hi  ,

    By default, [DNPR]EventPollPeriodDefault = 60 sec. It looks like that the I/O device was offline after 60 seconds. I am not sure if your device supports unsolicited events. Try [DNPR]AutoUnsolicitedEnableDefault = 0 and see if it would solve the issue. If not, please reach out to the technical support for further troubleshooting.

    Regards,

    Jacky

Reply
  • Hi  ,

    By default, [DNPR]EventPollPeriodDefault = 60 sec. It looks like that the I/O device was offline after 60 seconds. I am not sure if your device supports unsolicited events. Try [DNPR]AutoUnsolicitedEnableDefault = 0 and see if it would solve the issue. If not, please reach out to the technical support for further troubleshooting.