Real values in AVEVA communication Modbus

Hello,

I established a Modbus TCP/IP communication between AVEVA Plant SCADA and a M221 PLC from Schneider.

Everything works correct until I want to exchange some Real values. I use MODNET30 Protocol and use %MW to determine the addresses but I think it's necessary to swap somehow the values in SCADA, because:

My Real TAG in Aveva have the address %MW38 when I write value 1 from AVEVA to M221 I receive in M221 at the address %MW39 value 16236

AVEVA value: %MW39 = 1.1 in PLC at %MW38 = -13107 and %MW39 = 16268

Can somebody offers me some support on this problem?

Also if I need to comunicate with M240 what Protocol it's necessary to use? MODNET30 ?

Parents
  • I'm a bit confused from your second example: do you have a REAL variable definition with address %MW39 as well as %MW38?
    REALs take up two consecutive modbus registers, so a REAL at %MW39 should not exist if you already have a REAL at %MW38.

    I'm not too familiar with M221 PLCs, but with modbus devices in general you first have determine whether you have
    a) a register shift problem (0-based addressing vs. 1-based addressing)
    b) a byte order problem
    or both...

    To determine if you have a register shift issue, you should define an INT variable on both sides at equal address, and test with small and large values (say 1 and 10000). If writing to these variables from SCADA results in value changes in other addresses (N + 1 or N - 1) in the PLC then you have to switch to a MODNET variant with a different base address, in your case from MODNET30 to MODNET20.

    If your INT variables work fine, but your REAL and/or LONG values are garbled, then you have a byte-order problem, which you can fix using [MODNET] parameters. For REALs you can use [MODNET]FloatMode (as Jacky mentioned) and for LONGs you can adjust [MODNET]LongDataType.

    Please pay attention to Jacky's note however: both parameters mentioned here cannot be used for MODNET30 and MODNET20 protocol variants. You will have to switch to a standard MODNET, MODNET1, MODNET2, or MODNET3 variant in this case, and you have to change your variable address notation as well because these standard variants do not support %MW notation (change %MW38 to 400038 in your example).

Reply
  • I'm a bit confused from your second example: do you have a REAL variable definition with address %MW39 as well as %MW38?
    REALs take up two consecutive modbus registers, so a REAL at %MW39 should not exist if you already have a REAL at %MW38.

    I'm not too familiar with M221 PLCs, but with modbus devices in general you first have determine whether you have
    a) a register shift problem (0-based addressing vs. 1-based addressing)
    b) a byte order problem
    or both...

    To determine if you have a register shift issue, you should define an INT variable on both sides at equal address, and test with small and large values (say 1 and 10000). If writing to these variables from SCADA results in value changes in other addresses (N + 1 or N - 1) in the PLC then you have to switch to a MODNET variant with a different base address, in your case from MODNET30 to MODNET20.

    If your INT variables work fine, but your REAL and/or LONG values are garbled, then you have a byte-order problem, which you can fix using [MODNET] parameters. For REALs you can use [MODNET]FloatMode (as Jacky mentioned) and for LONGs you can adjust [MODNET]LongDataType.

    Please pay attention to Jacky's note however: both parameters mentioned here cannot be used for MODNET30 and MODNET20 protocol variants. You will have to switch to a standard MODNET, MODNET1, MODNET2, or MODNET3 variant in this case, and you have to change your variable address notation as well because these standard variants do not support %MW notation (change %MW38 to 400038 in your example).