Hi All,

Currently I have a ⁠OMRON CJ2M CPU14 with OMRON CJ1W-ETN21. The plc programmer told me that he converted the FINS to Modbus TCP/IP so I tested to use Modicon- MBTCP all of the drivers but not working. Is there any solutions to overcome this issue or what items that I need to look for?

Parents
  •  Hi  ,

    I suggest that you download a copy of Modbus Tester from Schneider Electric website - https://www.se.com/au/en/faqs/FA180037/ (how-to video is also available on this website. the tool is very easy to use), and use this tool to confirm that the configured PLC supports Modbus TCP/IP. If the test result is positive, it could be misconfiguration in your OI server.

    Hope this would help.

    Regards,

    Jacky

  • Does the application same functionality as modscan32?

  • Both of them are used for testing connectivity with the devices of Modbus protocol. I am not an expert of using OI drivers. But I did test OI PCS Plugin with MBTCP driver talking to ModSim devices.

    Here is the workflow of configuring MBTCP driver talking to ModSim and hope it would help you.

    • Launch Operations Control Management Console (type in aaSMC from Windows Start Menu)

    • Locate Modicon - MBTCP and then right mouse click on node Port and select Add ModbusBridge Connection, as shown below

    • Give the connection a name and fill in the network address and port number as shown below, and then click on Save on the top-right menu.

    • Right-mouse click on the newly created connection and select Add ModiconMicro Connection as shown

    • In the parameters tab, give PLC Unit Id as shown below, the same as defined in ModSim32

    • In Device Groups tab, right-mouse click on grid and add a group with Interval = 1000 ms. Save the changes

    • Start MBTCP service.

    • Here is the test result

    If you are still unable to get the communication going with your OMRON PLC, you should contact Technical Support for further troubleshooting.

    Regards,

    Jacky

Reply
  • Both of them are used for testing connectivity with the devices of Modbus protocol. I am not an expert of using OI drivers. But I did test OI PCS Plugin with MBTCP driver talking to ModSim devices.

    Here is the workflow of configuring MBTCP driver talking to ModSim and hope it would help you.

    • Launch Operations Control Management Console (type in aaSMC from Windows Start Menu)

    • Locate Modicon - MBTCP and then right mouse click on node Port and select Add ModbusBridge Connection, as shown below

    • Give the connection a name and fill in the network address and port number as shown below, and then click on Save on the top-right menu.

    • Right-mouse click on the newly created connection and select Add ModiconMicro Connection as shown

    • In the parameters tab, give PLC Unit Id as shown below, the same as defined in ModSim32

    • In Device Groups tab, right-mouse click on grid and add a group with Interval = 1000 ms. Save the changes

    • Start MBTCP service.

    • Here is the test result

    If you are still unable to get the communication going with your OMRON PLC, you should contact Technical Support for further troubleshooting.

    Regards,

    Jacky