Historian Variable Problem

Hello all,

I configured all my trend variables with "TRUE" in the column "Historize" and the values are inserted in the database correctly.

After that i configured some variables in variable list with "TRUE" in the column "Historize" but the values are not being entered in the database.

Any reason for not being in database?

Regards,

Parents
  • I found an answer here in the forum from Chris in october 2019:
    "The connector with only works with digital and strings data types for the variable tags. If you need a floating point, it would be better to setup a new trend tag and mark the historize field to "true". You could create a new string variable tag with a internal IO device(disk IO), then convert the floating point to a string, writing it to that new string tag."

Reply
  • I found an answer here in the forum from Chris in october 2019:
    "The connector with only works with digital and strings data types for the variable tags. If you need a floating point, it would be better to setup a new trend tag and mark the historize field to "true". You could create a new string variable tag with a internal IO device(disk IO), then convert the floating point to a string, writing it to that new string tag."