Hi,
Citect SCADA are using a long time to start because it failing to find USB Dongle license. So it hangs for 45-55 seconds on "Initalizing sub systems", before timing out and load Network license and finally start normally. Any way to bypass lookup for OEM USB Dongle on start-up?
in citect.ini this setting is already set:
WaitForConnectAtStartup = 0
Error message:
2020-10-12 12:55:25.532 +02:00 *** Citect process is starting up ***
2020-10-12 12:55:25.537 +02:00 Data Execution Prevention (DEP), has been enabled successfully
2020-10-12 12:55:25.592 +02:00 Protection: Provider DLL C:\Program Files (x86)\Schneider Electric\CitectSCADA 7.40\Bin\SentinelProvider.dll cannot supply a licence
2020-10-12 12:56:10.813 +02:00 Protection: Provider DLL C:\Program Files (x86)\Schneider Electric\CitectSCADA 7.40\Bin\LMBrickProvider.dll supplies an unrelated licence... ignoring
2020-10-12 12:56:10.818 +02:00 Protection: No suitable providers found
2020-10-12 12:56:10.818 +02:00 Licensing::OEM_DONGLE:oemDongleCheckLicence, ProtectionInitialise() failed with HRESULT(0x80004005)
2020-10-12 12:56:11.491 +02:00 Loaded _Library RDB; time 2020-10-08 11:27:16.
2020-10-12 12:56:11.573 +02:00 Alarm: Client loaded _Categor RDB; time 2020-10-08 11:27:16.
2020-10-12 12:56:11.806 +02:00 Licensing::LicenseProtection:ProtInit, licRunMode: 0x23eb
2020-10-12 12:56:11.822 +02:00 KerMain: Task ran for more than 1 sec: Task=MAIN, time=46261ms
2020-10-12 12:56:11.825 +02:00 Citect (PID 5448) Startup 7.40 Service Pack 1