ActiveX Combobox on wrong page

Hi everyone, 

Updating one app to 2018 r2 from citect scada 2015, an activex that displays a form with a list of items appears just in the main monitor. The client has a multimonitor function with two monitors. If the operator opens de form on the second display, the list appears on the main one.  

here the activex - 

  

any idea what is going on?

thanks. 

Parents
  • Hi Diego and Bernhard,

    Can you confirm the OS you are using?

    The Workspace (Situational Awareness) projects have ciText.comboboxes in them as part of the "Shelve Until..." form.

    Since you have 2018 R2 let's see if you can observe the same behaviour:

    Pre-reqs
    a. Make sure your computer has two or more monitors hooked up

    Steps
    1. Make your ExampleSA project Active
    2. Compile and Run the Setup Wizard
    3. On the Profile Setup step, select Use Profiles and then, Select "TWOMONITORSHD"
    4. Run the project up and you should hopefully see two workspaces displayed - one on each monitor.
    5. On Monitor1, select the 'Active Alarm' page
    6. Then, right click on any alarm and select 'Shelve Until..."
    7. The shelve form should appear with many combo boxes on it.
    8. Click on one of those and see if they display correctly.
    9. Repeat on the 2nd monitor's Active Alarm page.

    Cheers,

    bradley
Reply
  • Hi Diego and Bernhard,

    Can you confirm the OS you are using?

    The Workspace (Situational Awareness) projects have ciText.comboboxes in them as part of the "Shelve Until..." form.

    Since you have 2018 R2 let's see if you can observe the same behaviour:

    Pre-reqs
    a. Make sure your computer has two or more monitors hooked up

    Steps
    1. Make your ExampleSA project Active
    2. Compile and Run the Setup Wizard
    3. On the Profile Setup step, select Use Profiles and then, Select "TWOMONITORSHD"
    4. Run the project up and you should hopefully see two workspaces displayed - one on each monitor.
    5. On Monitor1, select the 'Active Alarm' page
    6. Then, right click on any alarm and select 'Shelve Until..."
    7. The shelve form should appear with many combo boxes on it.
    8. Click on one of those and see if they display correctly.
    9. Repeat on the 2nd monitor's Active Alarm page.

    Cheers,

    bradley