Citect SCADA 2018 R2 - Configure I/O Device Communications - Using Ethernet

Hello everyone,

I'm trying to configure the I/O Devices using an Ethernet connection. Follow the instruction as Citect SCADA web help from steps 1 to 3. I already finished it.

Move to the last step: Define the I/O Device units. The screen of the I/O Device setting shows that I have to fill in the address of the equipment again. The photo below

But the address I already define in step 2 of the instruction in the Ports form. The photo below

My question is: Do I need to fill the address again in the Configuration of I/O Device setting?

Best Regards

Canh

Parents
  • According to the TITCP driver help you don't need to set an address in the I/O Devices form. Just leave it blank.
    Are you sure you are using the correct driver for your situation? TITCP is for quite old hardware (Siemens SIMATIC TI 505 PLCs).
Reply
  • According to the TITCP driver help you don't need to set an address in the I/O Devices form. Just leave it blank.
    Are you sure you are using the correct driver for your situation? TITCP is for quite old hardware (Siemens SIMATIC TI 505 PLCs).