set(True = false)

Aveva Plant Scada 2020 R2 update 6 run time manager error

Hi,

I am running Aveva Plant Scada 2020 R2 update 6, while running the project  I am getting 'Runtime manager error' with notification as "cannot connect to the runtime manager service, ensure the service has been started".  I have tried starting runtime manager service manually but could not resolve the error.

below is the screenshot of error. 

/resized-image/__size/1048x588/__key/communityserver-discussions-components-files/1457/aveva-runtime-error.png

any guidance will be much helpful. 

regards,

Piyush

Parents Reply Children
  • In most cases, Runtime Manager will recover from this error. However, if you have many processes managed by Runtime Manager in an environment of lower spec hardware, you would experience this error. A workaround but not good one is to launch Runtime Manager, and then start up processes one by one manually.

  • Make sure that your machine is having minimum hardware specification as required by Aveva plant scada. my issue was resolved once I got the system with minimum hardware specification mentioned in help section of aveva plant scada