I am using Citect Scada 2016 . I have a USB key but when scada is run then its showing demo mode.
Please help us on very urgent basis. For reference attached a screenshot also.
I am using Citect Scada 2016 . I have a USB key but when scada is run then its showing demo mode.
Please help us on very urgent basis. For reference attached a screenshot also.
You could also run the Setup Wizard from the Studio. Make sure on this screen it is set for Server and Control Client so it is looking for a Full license (which you have). If you have Control or View-Only selected, it won't find the license since you don't have a control or v/o license.
Also, look in the Logs folder, and open syslog.dat in Notepad. At the bottom you should see messages about what is wrong with the license.