Kepware + Citect 2018 (W10)

Hi everybody!

I am starting to use Kepware OPC Server. In my laptop is OK. I export my Citect application and config.ini in factory computer, and the variables are in BAD state. In Kernel, OPC IODevice is OK. I open Kepware OPC client and data are OK.... What is happening??? Firewall is desactivated... Maybe there somo OPC parameters that I should configure and in my laptop windows vwrsion is not exactly as in Factory computer....

Parents
  • Check that [OPC]UseOPC2=1 is enabled.

    Run the computer setup wizard to make sure the IO Server is configured correctly.

    Is the Kepware OPC Server on the local machine (to the IO Server)? If it is remote, you will need to configure DCOM. See the online help for DOMC settings:

    gcsresource.aveva.com/.../OPC_DA_Server_DCOM_settings.htm

Reply