Writing values to devices using Modbus issue, roles and profile issue

Hello all, I have an issue when writing to devices using MODBUS, if I am using my configured profile and not citect.ini profile and the user that is signed in runtime was not the admin, runtime do not write values to devices on the network, but if I just signed in using the admin user in runtime, everything works fine and the values are being written to devices on network, but if I use the default citect.ini file, all users write values to Modbus devices and everything works fine.

note that, 1- I am not using any privileges, 2- I have no write roles on the tags I am trying to write on, 3- I had compared the citect.ini profile parameters and my profile parameters, the two are having some differences of course, but nothing seems to affect the writing on devices operation or role settings.

Parents Reply
  •  Hi  ,

    It appears to be configuration related. 

    • Windows or Plant SCADA authentication is used in your system?
    • How the profile is created? (should be created via Topology | Profiles in Plant SCADA Studio).
    • Have you used Configurator to set up the target machine?
    • Are you using Deployment?

    Take a look at [Client] section of the profile where it should have the following parameters

    • Clusters = [your clusters separated by comma]
    • ComputerRole = 1 (for control client and 2 for view only client)
    • PartOfTrustedNetwork = 1

    Hope the info here is helpful.

    ~Jacky