I am trying to use the alarm indicator on the genie but it does not show up on runtime when I trigger the alarm. Anyone has use this feature before?
Hi Mark ,
They are a little tricky to get going. I assume you have grouped a set of objects in Graphics Editor and enabled the Alarm Indicator feature?
See the help for more details: https://docs.aveva.com/bundle/plant-scada/page/1172183.html
Also note that the Alarm Indicator might not work if you have legacy graphics objects within the group.
From the help:
To configure an alarm indicator for an object group or Genie, you need to perform the following tasks:
Confirm that the required alarm priorities are assigned to an alarm category. See Categorize Alarms.
Define the display properties for the alarm priorities that an indicator will represent. See Configure Display Properties for an Alarm Priority.
For each object group or Genie, define the Alarm Indicator properties in Graphics Builder. See Alarm Indicator.
Let us know how you get on and if you require any further assistance.
Kind regards
Olivier
On top of Oli's reply, I assume you are using Equipment and that your alarms are tied to the equipment? Alarm Indicators only work with Equipment.
A lot of the items mentioned by Oli are pre setup if you use the sa_style_1_multires starter project.
Hi Olivier, I got this working yesterday. I forgot to setup the alarm categories. I had the alarm priorities setup but I forgot to configure the alarm categories.
thanks for the response.
Great to hear you got it up and running. The initial setup is a bit more involved than we would have liked, but it is worth the investment of effort.