How to connect the OPC Client with Matrikon OPC DA Simulator?

I was able to reach my production node from my plant node where I have the Matrikon application. The following picture is from my plant node, where I have the OPC

In my production node I'm able to see the tags of my OPC

Finally when I go to my Engineering node, I'm unable to reach the tags, I can't see them. I tried writing its paths in a lot of different ways but nothing. Any idea on how to make this work?

I tried with several associated attributes with a specific scan group, but nothing it doesn't seem to be the rigth path.

Any idea on why could this happen?

Thanks!

Regards,

Pablo.

Parents
  • Hi Pablo!

    I Agree with Rickard, Using OIGateway to talk to a OPC Server is introducing an unnecessary step in your system.
    But there are indeed reasons for doing so, If you want to avoid OPC over network you could have OI Gateway on the same node as the OPC Server and then use Suitelink to communicate remotely with OI Gateway, thus removing the OPC over network communication.

    But looking at your setup, the correct syntax for addressing on a remote object would be 

    OPCMatrikon_001.Random.OPC.DeviceGroup.Random.Int1

    Best way to verify is using object viewer.
    The use of Item references can be applied as a step 2, once you have verified connection, if needed.

    I note that you have checked the Use scan group as access path, this would break the above address, since it will insert the scangroup name in your final address, on a incorrect position, this selection could be applied on other OPC servers, not OI Gateway, since OIGateway has the "OPC.DeviceGroup" in the access path.

    I would omit this selection for simplicity in your testing.

    If you would set up the OPC object against the Matrikon OPC server, without the OIGateway involved, the config would be simpler.

    Please note that I'm avoiding naming my scangroup to Random to make the following example more clear.

    Then your syntax would look the following: OPCMatrikon_002.Fast.Random.Int1

    <DeviceIntegrationObject>.<ScanGroup>.<Path.Item>

    In this case you could apply the Use scan group as access path method.

    Naming your Access name "Random" and removing one part of your address.

    Result would then be: OPCMatrikon_002.Random.Int1

    <DeviceIntegrationObject>.<ScanGroup/Path>.<Item>

    I hope this clears things out.

    If you at this point still have issues connecting, it must be some security or network related issues, but since this is such a late reply to your post, you might have resolved all of your issues already Slight smile

Reply
  • Hi Pablo!

    I Agree with Rickard, Using OIGateway to talk to a OPC Server is introducing an unnecessary step in your system.
    But there are indeed reasons for doing so, If you want to avoid OPC over network you could have OI Gateway on the same node as the OPC Server and then use Suitelink to communicate remotely with OI Gateway, thus removing the OPC over network communication.

    But looking at your setup, the correct syntax for addressing on a remote object would be 

    OPCMatrikon_001.Random.OPC.DeviceGroup.Random.Int1

    Best way to verify is using object viewer.
    The use of Item references can be applied as a step 2, once you have verified connection, if needed.

    I note that you have checked the Use scan group as access path, this would break the above address, since it will insert the scangroup name in your final address, on a incorrect position, this selection could be applied on other OPC servers, not OI Gateway, since OIGateway has the "OPC.DeviceGroup" in the access path.

    I would omit this selection for simplicity in your testing.

    If you would set up the OPC object against the Matrikon OPC server, without the OIGateway involved, the config would be simpler.

    Please note that I'm avoiding naming my scangroup to Random to make the following example more clear.

    Then your syntax would look the following: OPCMatrikon_002.Fast.Random.Int1

    <DeviceIntegrationObject>.<ScanGroup>.<Path.Item>

    In this case you could apply the Use scan group as access path method.

    Naming your Access name "Random" and removing one part of your address.

    Result would then be: OPCMatrikon_002.Random.Int1

    <DeviceIntegrationObject>.<ScanGroup/Path>.<Item>

    I hope this clears things out.

    If you at this point still have issues connecting, it must be some security or network related issues, but since this is such a late reply to your post, you might have resolved all of your issues already Slight smile